Posted: 11:42am 09 Aug 2020
  TassyJim said  According to https://github.com/cpetrich/counterfeit_DS18B20
Your rom code is wrong due to the "20 02" last two numbers which should be zeros.
from the above link:
"If the ROM does not follow the pattern 28-xx-xx-xx-xx-00-00-xx then the DS18B20 sensor is a clone [5]."
and
"References
5. Own investigations 2019, unpublished."
the only statement about the content of the ROM made by the DS18B20 datasheet is:
"The least significant 8 bits of the ROM code contain the DS18B20’s 1-Wire family code: 28h. The next  48  bits  contain  a  unique  serial  number.  The  most  significant 8 bits contain a cyclic redundancy check (CRC) byte  that  is  calculated  from  the  first  56  bits  of  the  ROM  code."
based upon the DS18B20 datasheet, and without further input directly from Maxim, i'd find it hard to accept as gospel the "00 00" assertion; Maxim and/or DS could have in the past released any (large or small) number of DS18B20 with non-zero values in the 6th and 7th byte of the ROM.
i also have doubts about the forensic usefulness of the default contents of EEPROM - these values could innocently be changed by Maxim during manufacture and testing, during sample testing post-manufacturing, or by anyone in the supply chain who may have wished to test devices they handled. Maxim may have a number of plants capable of manufacturing DS18B20, and different plants could use their own individual testing and calibration routines that leave the EEPROM contents in set to a pattern identified as 'fake' .
apart from abnormal behaviour (including inaccuracy), the only sure way to identify a non-maxim part is to split the case open and examine the silicon die.
rob   :-)
Edited 2020-08-09 21:47 by robert.rozee
Posted: 12:13pm 09 Aug 2020
Hi Rob, All,
I have been wondering about the ROM as surely if you go to the effort to create a ‘clone’ could you not just clone the ROM code.
IF the one I bought from Jaycar is a fake it seems to have an almost identical temperature report to the genuine one.. (see my previous post with the two chips tied together.)
What is the zero degrees issue?  I can test them in a fridge/freezer/ice if you like.
Posted: 12:22pm 09 Aug 2020
  bigmik said  What is the zero degrees issue?
Paul_L once suggested to me that a very good way of testing/comparing perhaps dodgy waterproof DS18B20s was to put crushed ice in a glass, pour in a modest amount of chilled water, wait a few minutes for the ice to bring the water to very close to freezing, and insert the probes. That should be very close to 0C if you have the mix right, and a well-established universal calibration point.
Posted: 09:49pm 09 Aug 2020
Rob, you left out the bit about conversion times
  Quote  Based on the timing for 12 bit conversion, your device is group A2.
While I agree that the rom code 'could' be valid, it is unlikely in the extreme that Maxim will have produced a batch of chips that do the conversions in half the time, and then gone back to the normal time in subsequent batches.
I suspect that the clone manufacturers chose rom codes well outside the expected range to prevent the chance of duplicate codes being discovered in the immediate future.
The chips that Mick and I purchased from the Jaycar supply chain, all have slower timing than the usual times seen with known good chips, but the timing is still within published specs so 'could' be valid, but suspicious.
I buy through Ebay.
I expect clones, recycled chips, out-of-spec rejects...
Posted: 02:42am 10 Aug 2020
Hi Jim, All,
I did the ice water trick and both sensors reported the same readings within 0.25C all the way down from the ambient of 19.5C down to where they stopped updating at 0.5C
Mouser =  0.5   Jaycar =  0.5
The Jaycar unit seems to respond quicker to the change but only by the 0.25C then the Mouser unit caught up and they were together again until the Jaycar once again responded to drop before the Mouser one
As far as I can tell the 2 sensors as are accurate as each other.
It took a good 10 minutes for both units to settle at 0.5C
Kind Regards
Paul_L
Posted: 02:40am 14 Aug 2020
Funny thing about standards -- most of them aren't standardized -- except for the ice point of water.
It works best if you use distilled water (filtered rain water?), use an insulated coffee mug, ice chips not big ice cubes, stir the ice water for 30 seconds before inserting the probe, and insert the probe in the center of the mug without touching the sides or bottom. You should be able to achieve within 0.2°C of a true 0°C easily.
Paul in NY
Posted: 03:04am 14 Aug 2020
Hi Paul,
I used filtered ice water from our fridge and ice dispenser...  After about 15min neither sensor dropped below 0.5c
I actually did another test that I didn’t report, I used a can of freeze spray and they once again followed each other within 0.5 and 0.25C (dropping was a bit more inconsistent (no more than 1.5C but I put that down to me spraying one more than the other chip, it is hard to equally spray each DS18B20 even though I bound them together)...
At about -27.5C (a bit like a Polak summer??) I stopped and let them both recover and the spread between the known good Mouser and the suspect Jaycar chip was no more than 0.25 99% of the time with the odd one 0.5 difference  between chips and quite often reading Exactly the same.
My conclusion is that the Jaycar chip IF it is a fake is an extremely good fake and is most definitely suitable to be used as a DS18B20.
Kind Regards,
Paul_L
Posted: 05:23pm 14 Aug 2020
I don't understand why you guys go chasing the cheapest questionable source for these sensors. You're probably buying sensors that didn't pass final inspection. I suspect that the production yield after final inspection is less than 30%!
Bandgap sensors are difficult to make, requiring the calibration of the current density in two p-n diode junctions and measuring the difference between them. Why would you deliberately buy seconds when Mouser has over 3,000 of the real thing in stock at a price of < $4.00 each.
The only difficult part is finding an appropriately sized closed end stainless steel or copper tube to insert the TO92 case into, or just mounting them by their wires on a little terminal board.
Paul in NY
Posted: 03:44am 15 Aug 2020
Hi Paul,
The object is NOT to buy cheap it is to determine exactly what you will get for your money.
It is very confusing, for instance this listing from Mouser.
Mouser DS18B20
Includes 2 pages of offerings for DS18B20,
'Manufacturers' include many different sources.
For example
Seeed Studio
Maxim
Adafruit
Sparkfun
DFRobot
ANAVI Technology
DLP Design..
Then Mouser has a fairly expensive freight cost To AUS unless you spend $60 which I do when I buy from them.
Mind you I really like Mouser I get my parts usually 3-4 days after I order which is fantastic coming from the `REAL' antipodes.
Here in Aus we really are stuck with RS Components (great to deal with and free freight no matter order QTY), but often have to buy in bags of 5, 10 or more.
Element14 which offers free freight over I think $50.
Both the above are generally (not always) expensive prices and I have found recently that even though they say a qty is in stock, often they are placed on back order which could be 2-3 months away.
Then there are Jaycar and Altronics who whilst cheaper have a very limited repertoire of stock but they are generally in range of almost everywhere, if you are in the cities.
Then there is really only a smattering of other suppliers with the stuff we tinker around with and mostly do not stock much at all.
Kind Regards
Posted: 12:45am 10 Mar 2025
TassyJim's test program with some mods for the PicoMite.
'DS18x20 test code by TassyJim
' Input "Type Pin number ",PinNbr
Input "Type PicoMite GPxx number for the DS18B20 (include the GP) "; GPPin$
Dim INTEGER PinNbr = MM.Info(pinno GPPin$)
Print
Print
Print "Family name: ";FamilyName$(PinNbr)
Print "Rom Code:    ";getRomCode$(PinNbr)
Print "ScratchPad:  ";getScratchpad$(PinNbr)
If powerMode(PinNbr) Then
  Print "Power mode   External"
Else
  Print "Power mode   Parasitic"
EndIf
Print
For n = 9 To 12
  Print
  x = setResolution(PinNbr, n)
  Timer = 0
  Print "Temperature: ";getTemp(PinNbr);" ";Timer;"mS,";n;" bit"
Next n
Print : Print "Tempr() without start", TEMPR(PinNbr)
TEMPR START PinNbr,0 : Print "Tempr Start Pin,0", TEMPR(PinNbr)
TEMPR START PinNbr,1 : Print "Tempr Start Pin,1", TEMPR(PinNbr)
TEMPR START PinNbr,2 : Print "Tempr Start Pin,2", TEMPR(PinNbr)
TEMPR START PinNbr,3 : Print "Tempr Start Pin,3", TEMPR(PinNbr)
End
Function getRomCode$(PinNbr As INTEGER)
' get ROM Code - useful if you want more than 1 device on wire
Local INTEGER a1,a2,a3,a4,a5,a6,a7,a8
OneWire WRITE PinNbr,1,1,&h33 'read ROM code
OneWire READ PinNbr,0,8,a1,a2,a3,a4,a5,a6,a7,a8
getRomCode$ = Hex$(a1,2)+" "+Hex$(a2,2)+" "+Hex$(a3,2)+" "+Hex$(a4,2)+" "+Hex$(a5,2)+" "+Hex$(a6,2)+" "+Hex$(a7,2)+" "+Hex$(a8
,2)
End Function
Function getScratchpad$(PinNbr As INTEGER)
'ONEWIRE Write PinNbr,1,9,&h55,a1,a2,a3,a4,a5,a6,a7,a8  'read from scratchpad
OneWire WRITE PinNbr,1,2,&hcc,&hbe
OneWire READ PinNbr,0,8,a,b,c,d,e,f,g,h
getScratchpad$ = Hex$(a,2)+" "+Hex$(b,2)+" "+Hex$(c,2)+" "+Hex$(d,2)+" "+Hex$(e,2)+" "+Hex$(f,2)+" "+Hex$(g,2)+" "+Hex$(h,2)
End Function
Function powerMode(PinNbr As INTEGER) As INTEGER
' check whether power external (1) or parasitic (0)
OneWire RESET PinNbr
OneWire WRITE PinNbr, 1,2,&hcc, &hb4
OneWire READ PinNbr,4,1,powerMode
End Function
Function getFamily(PinNbr As INTEGER) As INTEGER
getFamily = Val("&h"+Left$(getRomCode$(PinNbr),2))
End Function
Function FamilyName$(PinNbr As INTEGER)
Local INTEGER fn
fn = getFamily(PinNbr)
Select Case fn
  Case 16
    FamilyName$ = "DS1820/DS18S20"
  Case 34
    FamilyName$ = "DS18S22"
  Case 40
    FamilyName$ = "DS18B20"
  Case Else
    FamilyName$ = "Unknown"
End Select
End Function
Function setResolution(PinNbr As INTEGER,r As INTEGER)
r = r-9
If r < 0 Then r = 0
If r > 3 Then r = 3
r = r*32+31
OneWire WRITE PinNbr, 1,5,&hcc, &h4E, &hFF,&hFF,r
End Function
Function getTemp(PinNbr As INTEGER) As FLOAT
Local INTEGER fn, t, T1, T2, a,b,c,d,e,f,g,h
Local FLOAT Value
power = powerMode(PinNbr)
OneWire RESET PinNbr                        ' reset before command
OneWire WRITE PinNbr, 8, 2, &hcc, &h44      ' start conversion
'read external when b goes high, for parasitic just wait
If power = 0 Then
  Pause 750
Else
  t = Timer
    If Timer - t > 1000 Then
      Value = 1000
      Exit Do
    EndIf
    OneWire READ PinNbr, 4 , 1 , b            ' conversion done?
  Loop Until b = 1
EndIf
If Value = 0 Then ' we have not timed out yet
  OneWire WRITE PinNbr, 1, 2, &hcc, &hbe      ' command read data
  OneWire READ PinNbr, 2, 2, T1, T2           ' get the data
  Select Case fn
    Case 16 'DS18S20 or DS1820
      If T2 And &h80 Then       'if MSB of T2=1 then negative
        'Read 12bit resolution and adjust
        'truncate 0.5deg value (or use integer division \)
        T1 = T1 And &hFE
        T1=T1 / 2                   'make whole degrees
        'add compensation values read from scratchpad
        T1=T1*16                  'make lsb 1/16 degree
        T1 = T1 -4 +(16 - g)    'add 12 bit value
        'take 2s complement
        T1 = (T1 Xor &hFF) + 1
        Value = -T1/16                'make decimal value in degrees
      Else                              'positive temp
        Value = T1 / 2                '9bit value
        T1 = T1 And &hFE      'truncate 0.5deg(or use integer division \)
        Value = T1/2- 0.25 + (16 - g) /16   '12 bit value
      EndIf
    Case 34, 40 ' DS18S22 or DS18B20
      If T2 And &b1000 Then       'negative temp
        'make 2s complement (1s complement+1)
        T2 = (T2 Xor &hFF)
        T1 = (T1 Xor &hFF)+1
        If T1=1 Then T2=T2+1        'add the carry if required
        Value = -((T2 And &b111) * 256 + T1) / 16
      Else                            'positive temp
        Value = ((T2 And &b111) * 256 + T1) / 16
      EndIf
    Case Else
      Value = 1000
  End Select
EndIf
getTemp= Value
End Function
And the output with my non-genuine units.
> RUN
Type PicoMite GPxx gp6
Family name: Unknown
Rom Code:    29 61 64 12 3D D4 A4 B8
ScratchPad:  7B 01 FF FF 7B FF FF FF
Power mode   External
ScratchPad:  FF FF FF FF FF FF FF FF
Temperature:  1000  17.838mS, 9 bit
Temperature:  1000  17.851mS, 10 bit
ScratchPad:  BD 80 FF FF AF FF FF FF
Temperature:  1000  17.827mS, 11 bit
ScratchPad:  7B 01 FF FF 7F FF FF FF
Temperature:  1000  17.815mS, 12 bit
Tempr() without start    23.625
Tempr Start Pin,0        23.625
Tempr Start Pin,1        23.625
Tempr Start Pin,2        23.375
Tempr Start Pin,3        23.375
> RUN
Type PicoMite GPxx gp7
Family name: DS18B20
Rom Code:    28 3F 44 57 04 E1 3C 4D
ScratchPad:  80 01 00 00 7F A5 A5 66
Power mode   External
ScratchPad:  80 01 FF FF 1F A5 A5 66
Temperature:  22.5  495.694mS, 9 bit
ScratchPad:  68 01 FF FF 3F A5 A5 66
Temperature:  22.75  495.831mS, 10 bit
ScratchPad:  6C 01 FF FF 5F A5 A5 66
Temperature:  22.75  495.681mS, 11 bit
ScratchPad:  6C 01 FF FF 7F A5 A5 66
Temperature:  22.8125  495.811mS, 12 bit
Tempr() without start    1000
Tempr Start Pin,0        1000
Tempr Start Pin,1        22.75
Tempr Start Pin,2        1000
Tempr Start Pin,3        22.8125
Edited 2025-03-10 10:50 by phil99
Posted: 02:18am 10 Mar 2025
Found time to test before leaving.
local retailer (Jaycar)
Rom Code:    28 AA 42 A3 41 14 01 D5
ScratchPad:  51 01 00 00 7F FF 60 10
Power mode   External
ScratchPad:  51 01 FF FF 1F FF 1F 10
Temperature:  21  109.795mS, 9 bit
ScratchPad:  50 01 FF FF 3F FF 3F 10
Temperature:  21  199.835mS, 10 bit
ScratchPad:  50 01 FF FF 5F FF 5F 10
Temperature:  20.875  379.825mS, 11 bit
ScratchPad:  4E 01 FF FF 7F FF 7F 10
Temperature:  21  739.858mS, 12 bit
Tempr() without start   21      210.887
Tempr Start Pin,0       21      110.06
Tempr Start Pin,1       21      209.799
Tempr Start Pin,2       21      409.839
Tempr Start Pin,3       21      809.776
> RUN
Known good.
Rom Code:    28 62 D8 F1 05 00 00 18
ScratchPad:  50 05 4B 46 7F FF 0C 10
Power mode   External
ScratchPad:  50 05 FF FF 1F FF 0C 10
Temperature:  22  94.519mS, 9 bit
ScratchPad:  60 01 FF FF 3F FF 10 10
Temperature:  21.75  169.149mS, 10 bit
ScratchPad:  5C 01 FF FF 5F FF 04 10
Temperature:  21.75  318.568mS, 11 bit
ScratchPad:  5C 01 FF FF 7F FF 04 10
Temperature:  21.625  617.607mS, 12 bit
Tempr() without start   21.75   210.933
Tempr Start Pin,0       22      109.848
Tempr Start Pin,1       21.75   209.812
Tempr Start Pin,2       21.75   409.785
Tempr Start Pin,3       21.625  809.801
The module purchased form Jaycar 5 years ago is slower that the specs but still just fast enough for the picomite code.
It may give errors in 9 and 10 bit resolution.
Posted: 05:51am 10 Mar 2025
More playing with Jim's program. Added some comments to help add unknown / non-genuine devices.
Print
Print
Else
EndIf
Print
For n = 9 To 12
  Print
  Timer = 0
  Print "Temperature: ";getTemp(PinNbr);"`C  ";Timer;"mS,";n;" bit"
Next n
Print :t=Timer : Print "Tempr() without Start", TEMPR(PinNbr);" `C",Timer-t;" mS"
TEMPR START PinNbr,0 :t=Timer :ds18=TEMPR(PinNbr):t=Timer-t : Print "Tempr Start pin,0", ds18, t
TEMPR START PinNbr,1 :t=Timer :ds18=TEMPR(PinNbr):t=Timer-t : Print "Tempr Start pin,1", ds18, t
TEMPR START PinNbr,2 :t=Timer :ds18=TEMPR(PinNbr):t=Timer-t : Print "Tempr Start pin,2", ds18, t
TEMPR START PinNbr,3 :t=Timer :ds18=TEMPR(PinNbr):t=Timer-t : Print "Tempr Start pin,3", ds18, t
Print
Print "*** The first RomCode value (a1) can be used to add extra devices to the FamilyName & getTemp functions"
Print "look for *** comments in those functions"
Print
End
'*** The first value returned (a1) can be used to add extra devices to the FamilyName & getTemp functions
'look for *** comments in those functions
,2)
End Function
End Function
End Function
End Function
Local INTEGER fn
Select Case fn
  Case 16  '&H10
  Case 34  '&H22
  Case 40  '&H28
  Case 41  '&H29
    FamilyName$ = "a non-genuine DS18B20"
  '*** Add extra cases here using the first value returned by Function getRomCode
  Case Else
End Select
End Function
r = r-9
If r < 0 Then r = 0
If r > 3 Then r = 3
r = r*32+31
End Function
Local FLOAT Value
If power = 0 Then
  Pause 750
Else
  t = Timer
      Value = 1000
      Print "*** Timeout ***"
      Exit Do
    EndIf
  Loop Until b = 1
'   Print Timer-t;" mS conversion time",
EndIf
  Select Case fn
        T1 = T1 And &hFE
        'take 2s complement
      Else                              'positive temp
      EndIf
        T2 = (T2 Xor &hFF)
      Else                            'positive temp
      EndIf
    Case 41 '&H29, a non genuine DS18B20
        T2 = (T2 Xor &hFF)
      Else                            'positive temp
      EndIf
    Case Else 'Unknown device
       ' *** use the output of this to create the scale factor of the unknown device
      'Value = 1000
        T2 = (T2 Xor &hFF)
        Value = -((T2 And &b111) * 256 + T1) / 1'<-This is where you put the scale factor
      Else                            'positive temp
        Value = ((T2 And &b111) * 256 + T1) / 1'<-This is where you put the scale factor
      EndIf
  End Select
EndIf
getTemp= Value
End Function
Example output. This one always reads 85° until after a Tempr Start pin,2 or 3 command then is ok till next power cycle.
> RUN
Type PicoMite GPxx number for the DS18B20 (include the GP) ? gp6
Family name: a non-genuine DS18B20
ScratchPad:  51 05 FF FF 7F FF FF FF
Power mode   External
Temperature:  85.0625`C   17.934mS, 9 bit
Temperature:  85.0625`C   17.951mS, 10 bit
ScratchPad:  A8 82 FF FF AF FF FF FF
Temperature:  680`C   17.91mS, 11 bit
Temperature:  85.0625`C   17.935mS, 12 bit
Tempr() without Start    85 `C   210.435 mS
Tempr Start pin,0        85      103.408
Tempr Start pin,1        85      203.84
Tempr Start pin,2        27.875  403.835
Tempr Start pin,3        27.875  803.819
> RUN
ScratchPad:  BF 01 FF FF 7B FF FF FF
Power mode   External
Temperature:  27.9375`C   17.964mS, 9 bit
Temperature:  27.9375`C   17.942mS, 10 bit
ScratchPad:  DF 80 FF FF AF FF FF FF
Temperature:  223`C   17.93mS, 11 bit
ScratchPad:  BF 01 FF FF 7F FF FF FF
Temperature:  27.9375`C   17.942mS, 12 bit
Tempr() without Start    27.875 `C       210.452 mS
Tempr Start pin,0        27.875  104.167
Tempr Start pin,1        27.875  203.82
Tempr Start pin,2        27.6875         403.821
Tempr Start pin,3        27.6875         803.819
Edit.
Prompted by Volhout's mention of the RP2350 pin issue I reduced the pullup resistor from 10k to 1.2k. Now the Rom Code value of a1 is &H28, as it should be. Was &H29.
It no longer reads 85°C in Jim's program but still requires an initial Tempr Start to get Tempr() to read correctly.
Edited 2025-03-10 20:08 by phil99
dddns
Posted: 11:41am 10 Mar 2025
Very helpful, many thanks for sharing! Will try later on
Posted: 04:33am 13 Mar 2025
For anyone with a DS18x20 device that doesn't work with Tempr() but does give sensible results with Jim's test program here is a Function derived from Jim's program.
Usage:-
 Print DS18x20(pin); "`C"
Or
 Temp = DS18x20(mm.info(pinno GPxx)) : Print Temp; "`C"
There are some comments to help adapt it to your device.
Function DS18x20(PinNbr As INTEGER) As FLOAT
' Extracted from DS18x20 test code by TassyJim
' Run that program and find the values that get your device to work.
' Copy those values into this Function
 Local INTEGER  t, T1, T2, done
 Local FLOAT Value=0
 t = Timer
 Do               'There should be a result in less than 1000mS
     Value = 1000 'standard error code
     Print "*** Timeout ***",
     Exit Do
   EndIf
 OneWire READ PinNbr, 4 , 1 , done       ' conversion done?
 Loop Until done
'  Print Timer - t;" mS conversion time", 'un-comment this to see how long it took
 If Value = 0 Then ' we have not timed out yet, so assume data is valid
      T2 = (T2 Xor &hFF)
      Value = -((T2 And &b111) * 256 + T1) / 16 'adjust this if the temp. is wrong
     Else                            'positive temp
      Value = ((T2 And &b111) * 256 + T1) / 16 'adjust this if the temp. is wrong
    EndIf
 EndIf
 DS18x20 = Value
End Function
Footnote added 2026-05-25 19:07 by phil99
There is a version of the above function specifically for the DS18S20 (Picomite) here
dddns
Posted: 07:52am 13 Mar 2025
Many thanks, I appreciate that!
I found, that my sensor is reliably answering after 600ms for 9 and 10 bit.
Knowing that, I code regarding it. Your function does not deliver earlier I guess.
So the best would be, that tempr() would have parameters to overwrite the datasheet defaults. Anyway, tempr() is not usable at all for me only tempr start.
So if I would really want to have the reading right now, maybe this function comes into play.In any case it's good to know how it is done and you gave the shortcut..thanks!
Posted: 08:07am 13 Mar 2025
If you post the results of TassyJim's test program here I may be able to adapt the Function to your unit.
As it is now the Function simply waits as long as necessary to get a reading (up to 1S). However if the 'x' in DS18x20 isn't 'B' or 'S' some changes may need to be made.
dddns
Posted: 08:27am 13 Mar 2025
First breakfast :)
Does it make a difference to?
tempr start(xx):pause xx:? tempr(xx)
dddns
Posted: 09:20am 13 Mar 2025
your function works very nice:
> RUN
473.178 mS conversion time      22.4375`C
473.595 mS conversion time      22.4375`C
473.79 mS conversion time       22.4375`C
473.998 mS conversion time      22.4375`C
473.204 mS conversion time      22.4375`C
473.388 mS conversion time      22.4375`C
473.607 mS conversion time      22.4375`C
473.853 mS conversion time      22.4375`C
474.02 mS conversion time       22.4375`C
473.178 mS conversion time      22.5`C
474.091 mS conversion time      22.5`C
dddns
Posted: 09:31am 13 Mar 2025
My 600ms I have lived with could be tuned a bit :)
Type PicoMite GPxx number for the DS18B20 (include the GP) ? gp15
Rom Code:    28 E9 CA 43 D4 E1 3C 7D
ScratchPad:  68 01 55 05 7F A5 A5 66
Power mode   External
ScratchPad:  68 01 FF FF 1F A5 A5 66
Temperature:  22`C   493.538mS, 9 bit
ScratchPad:  60 01 FF FF 3F A5 A5 66
Temperature:  22.25`C   493.751mS, 10 bit
ScratchPad:  64 01 FF FF 5F A5 A5 66
Temperature:  22.375`C   493.908mS, 11 bit
ScratchPad:  66 01 FF FF 7F A5 A5 66
Temperature:  22.4375`C   493.918mS, 12 bit
Tempr() without Start    1000 `C         209.257 mS
Tempr Start pin,0        1000    99.321
Tempr Start pin,1        22.25   204.063
Tempr Start pin,2        1000    399.376
Tempr Start pin,3        22.4375         803.979
dddns
Posted: 09:36am 13 Mar 2025
> do:tempr start gp15,1:pause 474:? tempr(gp15):loop
22.25
22.25
22.25
22.25
22.25
22.25
22.25
22.25
22.25
> do:tempr start gp15,1:pause 472:? tempr(gp15):loop
1000
1000
1000
1000
1000
1000
1000
     Page 6 of 7