Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9329
Posted: 12:20pm 18 Dec 2021
Copy link to clipboard 
Print this post

Apparently there is a problem with some capacitors formed on the die that are the wrong value. It wasn't considered to be important enough to redo the design, although there may be a correction if there are later releases.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
Volhout

Guru

Joined: 05/03/2018
Location: Netherlands
Posts: 6254
Posted: 12:36pm 18 Dec 2021
Copy link to clipboard 
Print this post

The difference between the running mean and John's algorythm is that the running mean first output value is the measured value. And it increases in accuracy. John's algorythm outputs 1/n  measured value as a first value, and after n iterations it is ramped up to the filtered value.

Some benefit for each method.
PicomiteVGA PETSCII ROBOTS
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 01:52pm 18 Dec 2021
Copy link to clipboard 
Print this post

  Volhout said  The difference between the running mean and John's algorythm is that the running mean first output value is the measured value. And it increases in accuracy. John's algorythm outputs 1/n  measured value as a first value, and after n iterations it is ramped up to the filtered value.

Some benefit for each method.


Yes - exactly. I did some comparison and found these values:

n       Pin(temp)       running mean    ewma
----------------------------------------------------
1       18.60978475     18.60978475     17.76693208
2       18.60978475     18.60978475     17.85121735
3       18.60978475     18.60978475     17.92707409
4       17.67328178     18.37565901     17.90169486
5       18.60978475     18.42248416     17.97250385
6       17.67328178     18.2976171      17.94258164
7       18.14153327     18.27531941     17.9624768
8       18.60978475     18.31712758     18.0272076
9       18.60978475     18.34964504     18.08546531
10      17.67328178     18.28200871     18.04424696
10      18.14153327     18.26796117     18.05397559
10      17.67328178     18.20849323     18.01590621
10      18.60978475     18.24862238     18.07529406
10      18.14153327     18.23791347     18.08191799
10      18.60978475     18.2751006      18.13470466
10      18.60978475     18.30856901     18.18221267
10      18.60978475     18.33869059     18.22496988


and here is the program which calculates both methods:

> list
' running mean - get better measurements

Dim M As float = 0.0 ' running mean
Dim ewma As float
Dim n As integer = 0 ' counter [0..Max]
Const Length = 10    ' up to 'Length' values are counting
Const weight = 0.1   ' weight of the new measurement

Print " n"," Pin(temp)"," running mean"," ewma"
Print "----------------------------------------------------"

ewma = Pin(temp)

While true do

 t = Pin(temp)
 n = Min(Length, n + 1)
 M = M + (t - M ) / n

 ewma = (1 - weight) * ewma + weight * t

 Print n,t,M,ewma
 Pause 1000

Loop


-andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4396
Posted: 02:52pm 18 Dec 2021
Copy link to clipboard 
Print this post

  Volhout said  John's algorythm outputs 1/n  measured value as a first value

That looks wrong.

John
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 03:55pm 18 Dec 2021
Copy link to clipboard 
Print this post

  JohnS said  
  Volhout said  John's algorythm outputs 1/n  measured value as a first value

That looks wrong.

John


Yes. The first value of Johns ewma is an initial measurement but this value is not printed, it is for initialization only. The second value is 90% of the first value and 10% of the new measuremnt added to the first value, iff weight = 0.1 . This process continues, 10% of every new value is added to 90% of the last sum.

I think the running mean is more accurate during startup (the first 10 values), in the long run both algos seem to be equal.

The bigger problem is that the Pin(temp) is jumping 1 degree between two measurements, so it can be used as a random number generator ;-)

-andreas
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4396
Posted: 04:06pm 18 Dec 2021
Copy link to clipboard 
Print this post

  andreas said  Yes - exactly. I did some comparison and found these values:

n       Pin(temp)       running mean    ewma
----------------------------------------------------
1       18.60978475     18.60978475     17.76693208
2       18.60978475     18.60978475     17.85121735
3       18.60978475     18.60978475     17.92707409


and here is the program which calculates both methods:

> list
' running mean - get better measurements

Dim M As float = 0.0 ' running mean
Dim ewma As float
Dim n As integer = 0 ' counter [0..Max]
Const Length = 10    ' up to 'Length' values are counting
Const weight = 0.1   ' weight of the new measurement

Print " n"," Pin(temp)"," running mean"," ewma"
Print "----------------------------------------------------"

ewma = Pin(temp)

While true do

 t = Pin(temp)
 n = Min(Length, n + 1)
 M = M + (t - M ) / n

 ewma = (1 - weight) * ewma + weight * t

 Print n,t,M,ewma
 Pause 1000

Loop


-andreas

Something odd in the values printed - looks like the initial Pin(temp) was oddly low. The chip bug?

John
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 04:26pm 18 Dec 2021
Copy link to clipboard 
Print this post

Something odd in the values printed - looks like the initial Pin(temp) was oddly low. The chip bug?


It looks like the first value was around 17.76
If have some picos here and will do some tests with them.



-andreas
Edited 2021-12-19 02:26 by andreas
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 06:47pm 18 Dec 2021
Copy link to clipboard 
Print this post

Now I have tested 5 different Picos, all processed the same way:

1. Cleared the flash: Clear_flash.uf2
2. Installed Picomite: PicoMiteV5.07.02b1.uf2
3. Started minicom 2.7.1 (my host = debian linux)
4. Started: XMODEM RECEIVE on the pico and pressed Ctrl A+S to start a transfer
5. Selected: Upload xmodem
6. Selected the "running mean.bas" and started it after transfer to the pico

The results are here   :

Pico#2

n       Pin(temp)       running mean    ewma
----------------------------------------------------
1       25.16530554     25.16530554     25.16530554
2       25.16530554     25.16530554     25.16530554
3       25.16530554     25.16530554     25.16530554
4       25.16530554     25.16530554     25.16530554
5       24.69705406     25.07165525     25.1184804
6       24.69705406     25.00922172     25.07633776
7       24.69705406     24.96462634     25.03840939
8       24.69705406     24.9311798      25.00427386
9       25.16530554     24.95719377     25.02037703
10      24.69705406     24.9311798      24.98804473


Pico#3

n       Pin(temp)       running mean    ewma                                                                          
----------------------------------------------------                                                                  
1       19.07803624     19.07803624     16.97090456
2       19.07803624     19.07803624     17.18161772
3       19.07803624     19.07803624     17.37125958
4       19.54628772     19.19509911     17.58876239
5       19.07803624     19.17168654     17.73768977
6       19.07803624     19.15607815     17.87172442
7       19.07803624     19.14492931     17.9923556
8       19.07803624     19.13656767     18.10092367
9       19.07803624     19.13006418     18.19863492
10      20.01453921     19.21851168     18.38022535


Pico#4

n       Pin(temp)       running mean    ewma                                                                          
----------------------------------------------------
1       20.48279069     20.48279069     17.95423267
2       20.01453921     20.24866495     18.16026333
3       20.48279069     20.32670687     18.39251606
4       20.48279069     20.36572782     18.60154353
5       20.01453921     20.2954901      18.7428431
6       20.48279069     20.32670687     18.91683786
7       20.01453921     20.28211149     19.02660799
8       20.01453921     20.24866495     19.12540111
9       20.01453921     20.22265098     19.21431492
10      20.48279069     20.24866495     19.3411625


Pico#5

n       Pin(temp)       running mean    ewma
----------------------------------------------------
1       16.73677881     16.73677881     15.05107347
2       17.2050303      16.97090456     15.26646915
3       16.73677881     16.89286264     15.41350012
4       17.2050303      16.97090456     15.59265313
5       16.73677881     16.92407941     15.7070657
6       16.73677881     16.89286264     15.81003701
7       16.73677881     16.87056495     15.90271119
8       16.73677881     16.85384168     15.98611796
9       16.73677881     16.8408347      16.06118404
10      16.73677881     16.83042911     16.12874352


So the temperature could be anything between 16 and 25 degrees. The ewma starts often with lower values but not everytime.

-andreas
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9329
Posted: 07:40pm 18 Dec 2021
Copy link to clipboard 
Print this post

Is the ADC for temp being initialised correctly? If only one channel is to be used it will be on GP26, if two then GP26 and GP27 etc. You might be reading a floating input.

See PicoMite manual page 74.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
matherp
Guru

Joined: 11/12/2012
Location: United Kingdom
Posts: 12186
Posted: 07:48pm 18 Dec 2021
Copy link to clipboard 
Print this post

The temperature is on a different ADC channel from the other inputs. These internal temperature measures are always pretty ropey

  Quote  The on board temperature sensor is very sensitive to errors in the reference voltage. If the ADC returns a value of
891 this would correspond to a temperature of 20.1C. However if the reference voltage is 1% lower than 3.3 V then
the same reading of 891 would correspond to 24.3C. You would see a change in temperature of over 4C for a small
1% change in reference voltage. Therefore if you want to improve the accuracy of the internal temperature sensor it
is worth considering adding an external reference voltage.
RP2040 Datasheet
4.9.
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9329
Posted: 08:20pm 18 Dec 2021
Copy link to clipboard 
Print this post

Ah... That makes sense. :)

It's always worth considering a 3v reference diode if there's any intention of using the ADC inputs for measurement anyway. That's why I've been leaving space for one on my boards whether it's needed or not. An LM4040 or NFC301 3V reference can be found for 90p or less.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 08:31pm 18 Dec 2021
Copy link to clipboard 
Print this post

  matherp said  The temperature is on a different ADC channel from the other inputs. These internal temperature measures are always pretty ropey

  Quote  The on board temperature sensor is very sensitive to errors in the reference voltage. If the ADC returns a value of
891 this would correspond to a temperature of 20.1C. However if the reference voltage is 1% lower than 3.3 V then
the same reading of 891 would correspond to 24.3C. You would see a change in temperature of over 4C for a small
1% change in reference voltage. Therefore if you want to improve the accuracy of the internal temperature sensor it
is worth considering adding an external reference voltage.
RP2040 Datasheet
4.9.


Ok, that is very interesting - thank you!

What I did was simply connecting a USB cable between Pico and PC. The PC was the source of power. The picos were without any other connection and all connected to the same USB port at the same PC.

Because its late here in germany I will go to bed now, but will take an external voltage for testing tomorrow. I have a WANPTEK NPS306W as power source and a RIGOL 1102Z oscilloscope for monitoring.

best regards and good night ;-)
-andreas
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 08:39pm 18 Dec 2021
Copy link to clipboard 
Print this post

  Mixtel90 said  Is the ADC for temp being initialised correctly? If only one channel is to be used it will be on GP26, if two then GP26 and GP27 etc. You might be reading a floating input.

See PicoMite manual page 74.


I used the internal temperatur measured by 'Pin(temp)' in Picomite.
-andreas
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9329
Posted: 09:32pm 18 Dec 2021
Copy link to clipboard 
Print this post

If you ground 3V3EN to shut down the SMPS and power the 3V3 rail directly (at 3.3v of course!) from a stable supply the readings should (in theory) be closer. :)

I'd missed the bit about Pin(temp) using a different ADC channel, sorry.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
vegipete

Guru

Joined: 29/01/2013
Location: Canada
Posts: 1193
Posted: 01:55am 19 Dec 2021
Copy link to clipboard 
Print this post

Since everyone likes pictures, here's a version for the CMM2, filtering a noisy square wave.



' Filter Test for CMM2
' written by Vegipete
'
' Uses running mean algorithm presented by Andreas
cls

' use following to plot a gaussian-ish distribution
'dim hist(400)
'for i = 1 to 100000
'  reading = int(RandGauss(32) * 400)
'  inc hist(reading)
'  line reading+200,579,reading+200,max(0,579-hist(reading)/4)
'next i
'end

text 50,400,"Filtering a Noisy Square Wave",,3
text 50,460,"WHITE : direct sample reading.",,3,,rgb(WHITE)
text 50,490,"RED   : 10 sample average.",,3,,rgb(RED)
text 50,520,"YELLOW: 50 sample average.",,3,,rgb(YELLOW)
text 50,550,"BLUE  : 100 sample average.",,3,,rgb(BLUE)

count = 0
square = 100
old_reading = RandGauss(32) * 40 + square
old_ave_10  = old_reading
old_ave_50  = old_reading
old_ave_100 = old_reading
average_10  = old_reading
average_50  = old_reading
average_100 = old_reading
do
 ' get new reading
 reading = RandGauss(32) * 40 + square

 ' calculate new averages
 inc average_10,  (reading - average_10 ) / 10
 inc average_50,  (reading - average_50 ) / 50
 inc average_100, (reading - average_100) / 100

 blit 1,50,0,50,MM.HRES-1,300  ' roll to the left
 line MM.HRES-1,0,MM.HRES-1,MM.VRES-1,1,rgb(BLACK)  ' clear

 ' plot graph
 line 798,old_reading,799,reading,1,rgb(WHITE) : old_reading = reading
 line 798,old_ave_10, 799,average_10,1,rgb(RED) : old_ave_10 = average_10
 line 798,old_ave_50, 799,average_50,1,rgb(YELLOW) : old_ave_50 = average_50
 line 798,old_ave_100,799,average_100,1,rgb(BLUE) : old_ave_100 = average_100

 inc count  ' generate square wave
 if count > 200 then
   count = 0
   square = 100 + (square = 100) * 200
 endif

loop

function RandGauss(samples as integer) as float
 local i,s
 for i = 1 to max(samples,4)
   inc s,rnd
 next i
 RandGauss = s / max(samples,4)
end function

Visit Vegipete's *Mite Library for cool programs.
 
CaptainBoing

Guru

Joined: 07/09/2016
Location: United Kingdom
Posts: 2171
Posted: 07:51am 19 Dec 2021
Copy link to clipboard 
Print this post

very nice
 
JohnS
Guru

Joined: 18/11/2011
Location: United Kingdom
Posts: 4396
Posted: 09:51pm 19 Dec 2021
Copy link to clipboard 
Print this post

andreas,

Thanks for those tests!

John
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 07:43am 20 Dec 2021
Copy link to clipboard 
Print this post

Hello,

thank you for all the good tips!

Today I looked at VBUS the power from the USB cable comming from the PC which powers the pico. Peter told me that "You would see a change in temperature of over 4C for a small 1% change in reference voltage".

I can see that the VBUS is not only changing by 1% but by 8.8% (440mV). The hihgest voltage is 5.24V and the lowest 4.80V. This explains all the problems I have with pin(temp) if it is based on this power supply.

Lesson learned: A computer is not a good voltage reference when doing measurements!


So the solution seems to be to get a reliable, stable power source (possibly by battery?), before doing any measuremnts.




-andreas
 
Mixtel90

Guru

Joined: 05/10/2019
Location: United Kingdom
Posts: 9329
Posted: 10:31am 20 Dec 2021
Copy link to clipboard 
Print this post

VBUS is the 5v supply from the USB. The reference voltage for the ADC is taken from the 3V3 line, fed from the SMPS. Because of the SMPS variation on VBUS or VSYS makes very little difference to the ADC reference.

Schematic

There is some filtering via C13 but variation on 3V3 still gets through. Have a look at the signal on VREF.
Mick

Zilog Inside! nascom.info for Nascom & Gemini
 
andreas

Senior Member

Joined: 07/12/2020
Location: Germany
Posts: 226
Posted: 02:10pm 20 Dec 2021
Copy link to clipboard 
Print this post

  Mixtel90 said  VBUS is the 5v supply from the USB. The reference voltage for the ADC is taken from the 3V3 line, fed from the SMPS. Because of the SMPS variation on VBUS or VSYS makes very little difference to the ADC reference.

Schematic

There is some filtering via C13 but variation on 3V3 still gets through. Have a look at the signal on VREF.


Do you mean pin 35?
  Quote  ADC_VREF is the ADC power supply (and reference) voltage, and is generated on Pico by filtering the 3.3V supply. This pin can be used with an external reference if better ADC performance is required.


I suppose this is a test point or output, but not an input for an external poser supply, correct? Or does "an be used with an external reference" mean that I put in some external power supply?

Btw. my external power supply has a "ripple" of some 80-120 mV (mostly 80 mV).
But I have some MCP1700 3.3V power regulators here, which I could use together with an 10uF elko to create a 3.3V reference.

-andreas
 