Forum Index : Electronics : 12 volt cable sizing
| Marcus20VT Regular Member Joined: 02/09/2008 Location: WalesPosts: 49 |
Hi all, I have a small pv and turbine system that I am thinking of charging a set of 12v deep cycle batteries to power a 12volt timer to control a 12V immersion heater element. Problem is, my system is out in my shed, and I obviously want to have the immersion element for the hot water inside my house. Therefore I would need to run cable from my shed to my house - about 10M or so. I have looked at the regs book for current carrying capacity and volt drop for cable for a 600W element. Erring on the side of caution, I'm getting that I would need 10mm twin and earth cable - surely that's not right is it????? |
| RossW Guru Joined: 25/02/2006 Location: AustraliaPosts: 495 |
10 sq mm cable is 1.678000 ohms per Km. You have 20m. (10m out and 10m back). 600W @ 12V is 50A 50A through 0.03356 ohms is 1.678 volts drop, wasting 84 watts. I'd be using heavier wire, or using a suitable inverter and 240V element. |
| norcold Guru Joined: 06/02/2011 Location: AustraliaPosts: 670 |
reuk.co.uk have a lot of info on wire sizes also a handy online calculator to show line losses. I find this calculator very handy, allows keeping the expense of long runs of copper cable down without going to an expensive overkill. Basically it is an online calculator that does what RossW has, you just input the voltage, current draw and cable length and the loss you are prepared to accept in percentage. Very handy as is a lot of info on that site. We come from the land downunder. Vic |
| Fred Bloggs Newbie Joined: 21/09/2010 Location: United KingdomPosts: 2 |
Hi I've been a silent member of this forum for a while so here goes with first post. 'Just noticed you want some method of checking out cable sizes, I did a excel spread sheet a couple of years ago that works out volt drops etc for any size cable upto 90mm2 single core at any voltage. I would post it on this forum but have just noticed that you cannot add an attachment, or am I being stupid
Best Regards Fred |
Hi Fred You can attach ZIP files. Zip it up and use the file upload button to upload it.
Welcome to the forum too, I see you've been a member for some time. Glenn The best time to plant a tree was twenty years ago, the second best time is right now. JAQ |
Glenn Thanks for that, I didn't realise what the symbol was for! So here goes 2011-07-21_223153_cable_calculator.zip Best Regards Fred Ps the spreadsheet was done in office 2003! |
Thanks for that Fred Opens in Open Office just fine too
You sure can appreciate why a higher battery voltage is better. Smaller wire for the same power. Glenn The best time to plant a tree was twenty years ago, the second best time is right now. JAQ |
| Bub73 Senior Member Joined: 10/12/2009 Location: United StatesPosts: 116 |
Thanks Fred; Works in Open Office under linux just fine for me also. I've been working on a spread sheet for blade length , using Hugh's formula and will share it when finished Bob |
| Warpspeed Guru Joined: 09/08/2007 Location: AustraliaPosts: 4406 |
An easy way to work this out for yourself, you only need to remember one number. A one metre length of rectangular copper bar 1mm x 1mm has a resistance of .0172 ohms (at 20C) So 30 metre stretch of 10 mm^2 (is actually 60m of wire). 60 m of 1mm ^2 wire would be .0172 x 60 = 1.032 ohms. If 10 mm ^2 wire is used instead, it would be one tenth the resistance or 0.1032 ohms. If you can remember the .0172 number, it is then dead easy to work out the resistance of any length of any gauge of copper wire. 600 watt hearting element is 50A at 12V or 0.24 ohms at full power. Total resistance of wire plus element 0.3432 ohms. Total current at 12v input 34.97 Amps Voltage drop across wiring 3.61 volts Voltage at heating element 8.39 volts Cheers, Tony. |