Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1664
Posted: 11:45pm 29 Apr 2018
Copy link to clipboard 
Print this post

Hi All,

Just ran the meter over the 12 panels I got the other day.

Specs are,
Voc=37.5V
Isc=9.0A

Pretty much getting a reading in spec with only a small variation.
Getting about 7.8A on average.

Except for 1 Panel.

Think it was about 24.5V Voc & 7.8A Isc.

Nothing visually obvious, & Didn't get a chance to opened the junction box yet.

Does this behaviour sound typical of a Diode failure, possibly shorting out one of the strings on the panel?

Will open it up later & test, but curiosity needs some feedback sooner.

Cheers

Phil.
 
yahoo2

Guru

Joined: 05/04/2011
Location: Australia
Posts: 1166
Posted: 12:02am 30 Apr 2018
Copy link to clipboard 
Print this post

a third of your panel is not in circuit, it sounds like it has been wired incorrectly somehow.
I'm confused, no wait... maybe I'm not...
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 12:14am 30 Apr 2018
Copy link to clipboard 
Print this post


Last panel box I opened had 3 Diodes so maybe being a 3rd is out it could be a Diode or connection there.

The Panel I opened was a 250 and I see all of yours are about that size so maybe you will be in luck and it will be an easy fix.

If the panel is buggered, still good for other uses.
I have 2 Shattered panels on the roof of my shed that drive the car fans for keeping the shed cool and the light for my Aeroponic system. Soon going to put that in my little greenhouse I just bought to play with.

Being that it is outputting 24V, you could use it for battery charging or top up on the mower and other things.
 
Boppa
Guru

Joined: 08/11/2016
Location: Australia
Posts: 814
Posted: 02:23am 30 Apr 2018
Copy link to clipboard 
Print this post

Its not uncommon for diodes to fail in high temps at full capacity, and often go O/C
Definitely sounds like a string has failed, and I'd bet on the diode has gone
Easy to check and easy to replace if it has
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1664
Posted: 05:12am 30 Apr 2018
Copy link to clipboard 
Print this post

Opened up the terminal block; potted in silicone.





Figured the 3rd diode must be SC, so cut it's leg.

Notice how the lead fell free.

I could measure 12V across each string, but once the diode was out I got 0V from the panel.

I can get full Voc at the top green mark, but nothing at the screw below it.

It should be present there I think?

Seems the diode may have been ok, just poorly terminated, hence the heat signs, but the real problem may have been lack of continuity between the two bits marked in green.

Will wait for the silicone solvent to work a bit & then have a better look.

Phil.


Edit, Closer view.



Edited by Phil23 2018-05-01
 
yahoo2

Guru

Joined: 05/04/2011
Location: Australia
Posts: 1166
Posted: 10:29am 30 Apr 2018
Copy link to clipboard 
Print this post

  yahoo2 said   a third of your panel is not in circuit, it sounds like it has been wired incorrectly somehow.


Actually I think I am wrong, you should get full voltage and restricted amps with a wiring fault. so if you have a terminal with full voltage perhaps you have a high resistance connection somewhere.
I'm confused, no wait... maybe I'm not...
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1664
Posted: 09:00pm 30 Apr 2018
Copy link to clipboard 
Print this post

  yahoo2 said  
  yahoo2 said   a third of your panel is not in circuit, it sounds like it has been wired incorrectly somehow.


Actually I think I am wrong....


Nope,

Your were on the mark. The last 1/3 was out of circuit due to a very poor connection at the top green mark when the strip from the cells comes thru the slot in the terminal.

Output from the other 2 was getting there via the 3rd diode, despite the fact that it's spot weld had failed.

Phil.
 
Phil23
Guru

Joined: 27/03/2016
Location: Australia
Posts: 1664
Posted: 09:08pm 30 Apr 2018
Copy link to clipboard 
Print this post

Fault was exactly as shown here...



 