tell me if i have this correct...

panel: Sharp Nu185A1H

http://www.sharp.net.au/product-catalogue/products/NU185A1H/

VOc = 30.2volt (@25 Deg)
temp coefficient of Voc -0.104 V/DEG,c

SO....

if the VOc at 25 deg is 30.2v
then at 0deg the voc would be 25x.104 =2.6 volts increase
30.2v + 2.6v
thus VOc at0 deg would be 32.8V (open cct)

(assuming 1kw/M2 irradance)<<---perfect conditions...)

all this so i can work out a cold sunniy morning max open cct voltage)

Cheers
 
Tinker

Guru

Joined: 07/11/2007
Location: Australia
Posts: 1904
Posted: 01:58pm 15 Mar 2012
Copy link to clipboard 
Print this post

So... what is the reason for this precise knowledge of the open cct voltage?

Somehow a gut feeling tells me that you won't get 1Kw/sqm when its that cold in the morning.
Klaus
 
rgormley
Senior Member

Joined: 22/02/2006
Location: Australia
Posts: 245
Posted: 07:29pm 15 Mar 2012
Copy link to clipboard 
Print this post

hi tinker, thanks for the reply, you are correct not ever reaching these max values.
just would like to know if my "theory" maths is correct...

AND I will be running close to my 500Vdc max input on my string and i want to add one more panel.

so am looking at possible worse case voltage spike.

early morning cold, edge effect, grid goes of etc etc then the inverter gets hit with a high voltage from cold panels.

panels will be (QTY X 16) at 25Deg-c (30.2Vdc x 11 = 483Vdc)

my inverter is max 500Vdc input.

I could go 2 strings but inverter only has one string input.

So i would have to parallel the panels and it`s a lot of work to get to the cabling. SO i`m doing it all in series. (one string) hence the higher voltage

(PS my area`s record low in 2.7 deg-c,)

 
Tinker

Guru

Joined: 07/11/2007
Location: Australia
Posts: 1904
Posted: 01:40pm 16 Mar 2012
Copy link to clipboard 
Print this post

Fair enough, that explains it perfectly now that I know that you are aiming for a rather high DC max voltage.
BTW, your record low temp suggests you live in Perth - correct
Klaus
 
rgormley
Senior Member

Joined: 22/02/2006
Location: Australia
Posts: 245
Posted: 08:14pm 16 Mar 2012
Copy link to clipboard 
Print this post

Altona Meadows (Melbourne)

The Melbourne radar is about 2-3 k`s from where i live

from the weather zone web

***************************
lowest on record
2.7°C
26th 2005

*****************************

don't think i`l have an issue as these low temps are early in the morning and the sun prolly has not risen as yet. so not much light on the panels....
 
Georgen
Guru

Joined: 13/09/2011
Location: Australia
Posts: 462
Posted: 12:42am 19 Mar 2012
Copy link to clipboard 
Print this post


Could probably have thermometer coupled with some shading device that could also keep an eye on strength of solar output.

Or another device to protect solar PV system should this rare event to occur.

George
 
VK4AYQ
Guru

Joined: 02/12/2009
Location: Australia
Posts: 2539
Posted: 01:04pm 19 Mar 2012
Copy link to clipboard 
Print this post

Checked mine on a cold clear morning 15 C open circuit volts 36.2 open circuit no load ,by 10 am 28 C OCV 34.

it is a different brand of panels to yours.

Bob
Foolin Around
 
daveames
Newbie

Joined: 19/09/2009
Location: United States
Posts: 30
Posted: 09:49am 20 Mar 2012
Copy link to clipboard 
Print this post


I'd be worried about all the over voltage flags stored to memory every time the temp goes below 15*C..I believe this will still happen with VERY little sun light.

Should we need any warranty work with the inverter in the future there may be some splannin' to do.

Dave
 