Forum Index : Solar : Inline mc4 fuse

     Page 2 of 2    
Author Message
Madness

Guru

Joined: 08/10/2011
Location: Australia
Posts: 2498
Posted: 11:01am 11 Apr 2018
Copy link to clipboard 
Print this post

  George65 said  
  Madness said   you are at serious risk of having a fire.


Sorry, I disagree completely.

If I can short the wires coming from the panels and they don't even heat up let alone burn, how am I going to have a fire? Fusing in that case is irrelevant.

The gauge of wire I am using is about 3 times the current rating of the panels output.
The voltage and amperage of the panels drops once it gets off it's curve or whatever you want to call it for a start further reducing the current. I can't speak for other peoples or commercial systems but I do know how I have done my own and I have tested this to know what I say.

If you don't believe me and want to put a wager on it to make it worth my while, I'll do a fair and honest Video to show you and put it up for all to see.
An 8Amp load is an 8A load be it put to work or be it a dead short. It's still 8A and if I am using wire rated at 27A.... It's not going to burn.

The video you linked to is also completely irrelevant to what I said.
Of course there is going to be severe arcing if you only switch one side. That was exactly NOT what I was talking about at all. I specifically said switch BOTH lines at the same time.
Is there a video of that we can look at to see what happens in THAT setup?
Maybe the breakers will only last 100 cycles instead of 10K like they would with AC but that's still OK to me and I doubt any system gets turned on and off under load that much in it's lifetime anyway.

I know the result will be different if you switch both sides simultaneously because I switched one of my arrays with 2.8 Kw going through it at about 380V several times this afternoon when I was moving some panels around without problem and I have probably switched it under load 20 or 30 times at least in total.

Again, I am using a breaker on both the pos and neg outputs from the panels, not just one side as one would do with AC. That makes a SIGNIFICANT difference in extinguishing the DC arc.

If you can find a demonstration where the breakers arc at similar output and setup to what I am using, then I will revise my position. Until such time as then or I see a problem first hand, I'll go with the repeated and problem free experience I have.


Sorry George but you are WRONG!

An AC breaker relies on the 0 crossing of the wave to extinguish the arc. When you turn off DC the current does not drop to 0 but continues and makes an arc just like you described. Turning off both positive and negative together just means 2 arcs and twice the problem. DC Breakers have a large gap and a magnet to pull the arc out of the breaker contacts. AC Breakers don't have the magnet and this is why they are not to be used with DC. The fire will start from within the breaker itself nothing to do with the wires they are simply delivering the power to the arc.

You are at risk of having a fire, I am just trying to give you some friendly advice, you are taking a big risk with your home and the lives of the people that live in it.Edited by Madness 2018-04-12
There are only 10 types of people in the world: those who understand binary, and those who don't.
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 11:37am 11 Apr 2018
Copy link to clipboard 
Print this post

  Madness said  
You are at risk of having a fire, I am just trying to give you some friendly advice, you are taking a big risk with your home and the lives of the people that live in it.


I appreciate the warning and the sentiment behind it but please understand, I have seen nothing to make me believe it. I don't mean that to be a smartarse, I mean it sincerely and honestly. This is a perfect example of a saying of mine, you can tell people things but getting them to believe it is a different thing. This is where I find myself with this.

Could you suggest the parameters of a test like the vid you linked to I could setup to demonstrate and enlighten myself of how these AC breakers can fail as you describe?

I have 5+ Kw of panels at my disposal I can easily tap into so if you could tell me what I have to do to light a couple of AC breakers up, i'd be happy to make the investment for the learning value and a great YT vid! It would be good to demonstrate to others whom may also be ignorant and disbelieving like myself.

As I said, I have done this repeatedly with around 2.8 Kw and a lot more load going through the Ac breakers I have and there hasn't been so much as a fizz. I don't want to be taking a position based on an ineffective parameter when possibly just a bit more power may make all the difference.
Knowing the facts is more important to me than being wrong so I'm interested to see this first hand and change my mind.

What would I have to do to light some AC breaker up to see what you are talking about and educate my ignorant self?

You may be please to know that the AC breakers I am using are for the systems on the shed. I now have 3 or 4 ( can't remember) proper dial type isolators from the used systems I bought. I am starting to install panels on the house and did intend to use these isolators on the 2 arrays I plan to put up. One will be 5 Kw and the other 4.

I have also arranged for a sparky to come put in a couple of heavy duty Circuits for the solar and will over rate that cable significantly being I can afford to as the cable run won't be too long and the guy is happy to sell me the cable by the meter at cost.
We are looking at 10mm to do a separate circuit for each inverter. Overkill but if I want to add more panels later, I will have the headroom to do so.
Still will have more than half the roof available.
 
Boppa
Guru

Joined: 08/11/2016
Location: Australia
Posts: 814
Posted: 01:43pm 11 Apr 2018
Copy link to clipboard 
Print this post

I was actually looking at making a 'solar powered stick welder' once I start building the new place- basically solar panels attached to a welding holder LOL

Most stick welders are between 30-60vdc, varying the current from 30a up to a hundred or more for things like truck chassis welding
So as a panel is a constant current source (like the better stick welders), I was thinking along the lines of having 10 or so 180w panels in parallel as a offgrid welder....
Might work, might not but be fun trying
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 02:57pm 11 Apr 2018
Copy link to clipboard 
Print this post


Wiring up 10 panels in Parallel sound like a real pain in the backside. You could put each or every 2nd one on a breaker to give yourself some amperage control.

Something I was thinking to give a go was making Chlorine.

I believe one takes a salt water soloution and passes a current through a couple of plates to convert the salt to Chlorine ( and a couple of other things helpful for cleaning).
 
renewableMark

Guru

Joined: 09/12/2017
Location: Australia
Posts: 1678
Posted: 09:16pm 11 Apr 2018
Copy link to clipboard 
Print this post

Well no wonder it's confusing, some breakers are manufactured bottom feed, others top feed and others have polarity markings top and bottom.
Read here
Cheers Caveman Mark
Off grid eastern Melb
 
Madness

Guru

Joined: 08/10/2011
Location: Australia
Posts: 2498
Posted: 09:30pm 11 Apr 2018
Copy link to clipboard 
Print this post

  Boppa said   I was actually looking at making a 'solar powered stick welder' once I start building the new place- basically solar panels attached to a welding holder LOL

Most stick welders are between 30-60vdc, varying the current from 30a up to a hundred or more for things like truck chassis welding
So as a panel is a constant current source (like the better stick welders), I was thinking along the lines of having 10 or so 180w panels in parallel as a offgrid welder....
Might work, might not but be fun trying


My 200A MIG welder operates under 30VDC but they are constant voltage rather than constant current like a stick welder. You can buy a inverter stick welder on Ebay for under $100 delivered, with a few mods the make good battery chargers also.

Here is a demonstration VIDEO of the difference between breaking a AC circuit and a DC circuit.
There are only 10 types of people in the world: those who understand binary, and those who don't.
 
Madness

Guru

Joined: 08/10/2011
Location: Australia
Posts: 2498
Posted: 09:32pm 11 Apr 2018
Copy link to clipboard 
Print this post

  renewableMark said   Well no wonder it's confusing, some breakers are manufactured bottom feed, others top feed and others have polarity markings top and bottom.
Read here


Mark you use the correct polarity on the side that supplies the current.
There are only 10 types of people in the world: those who understand binary, and those who don't.
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 01:06am 12 Apr 2018
Copy link to clipboard 
Print this post


I can't see why the breaker terminal orientation would make much difference anyway. Looking at the the breaker boxes and the isolators I have got with the used systems I have bought, the penetrations for the cable are all from the bottom and the wire goes up in the housing and to the top side of the breakers.

Can't see any need on the boxes I have to have to come in or out from the top. Go through the bottom side by side and take the cable to the other side of the breaker internally leaving the top of the switch box sealed so the water can run off and not have a way in.



Mad, did you see my question about creating the parameters for an AC breaker burn demonstration?
Nice and sunny here today and I'm not going anywhere so would be interested to give it a go.
 
Madness

Guru

Joined: 08/10/2011
Location: Australia
Posts: 2498
Posted: 02:39am 12 Apr 2018
Copy link to clipboard 
Print this post

To be honest George I can't be bothered if you think you can get away with it good luck to you.
There are only 10 types of people in the world: those who understand binary, and those who don't.
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 06:19am 12 Apr 2018
Copy link to clipboard 
Print this post

  Madness said   To be honest George I can't be bothered if you think you can get away with it good luck to you.


Sorry, that's a complete and utter cop out and you know it.

If you thought you would be proven right when push came to shove, you'd have no hesitation in saying "run this many volts at this many amps through this size breaker and do this" to prove your position.

That's always the test I use with fearmongering and excessive safety warnings, rather than avoid, actually Create the problem and see what happens when you do. It never is at all like the over hyped warnings predict or stands up to the parroted mantra's.

I'd do a test myself but without instructions, Know whatever I do would be deemed flawed with an endless myriad of manufactured flaws in the test when it didn't go up in smoke.

You are a far more knowledgeable and intelligent fella than I am mad but that does not mean you cannot be wrong or overly pedantic about some things.
 
renewableMark

Guru

Joined: 09/12/2017
Location: Australia
Posts: 1678
Posted: 08:27am 12 Apr 2018
Copy link to clipboard 
Print this post

DC breakers aren't dear so why not just use them?
here is an example
Cheers Caveman Mark
Off grid eastern Melb
 
Solar Mike
Guru

Joined: 08/02/2015
Location: New Zealand
Posts: 1138
Posted: 09:38am 12 Apr 2018
Copy link to clipboard 
Print this post

  renewableMark said   DC breakers aren't dear so why not just use them?
here is an example


They are good quality breakers, have used them myself, have quite strong blowout magnets inside to prevent arc's forming; unlike some of the other chinese brands marked as suitable for DC, but have no magnets inside at all.

New regs here in NZ means they are not allowed, as your average electrician doesnt know how to wire them up. However nothing wrong with them if wired correctly.

Mike
 
George65
Guru

Joined: 18/09/2017
Location: Australia
Posts: 308
Posted: 09:55am 12 Apr 2018
Copy link to clipboard 
Print this post

  renewableMark said   DC breakers aren't dear so why not just use them?
here is an example


If I need any more, I will get some. For the moment I'm OK with the isolators I have.

With this thread in mind, Today I went up the back and again with 2.8 Kw going through them, I turned off the AC breakers I have ( Wired through both poles) Several times.
Again, Not peep out of them.

If I saw anything to make me think they were not safe, I would change them. As said, they aren't exy but I have seen nothing to make me think wired up as I have them there is anything wrong with using them.

Again, I am NOT using them as just switching one side but as 2 poles breaking both outputs at the same time.
 
yahoo2

Guru

Joined: 05/04/2011
Location: Australia
Posts: 1166
Posted: 12:54am 13 Apr 2018
Copy link to clipboard 
Print this post

some brands have an identical innards in their AC breakers, like noark and sometimes they get sold real cheap in bulk.
I'm confused, no wait... maybe I'm not...
 